Hi all,
I need to replace the old fuse box in the garage with a CU and at the same time install a load balancing a fast charge outlet for electric vehicle.
Current installation has a sub panel in the house (40A) with type B MCBs: 20A for kitchen sockets and 32A for the garage supply. Main board is double RCD 80A/ 63A and DNO fuse is 100A.
10mm SWA cable underground to garage, approx 15m.
Plan is to move the kitchen sockets on to the main board (there is a spare), replace the adjacent garage sub panel for a 63A RCD panel with a 50A MCB, and replace the old fuse box in the garage with similar panel but with a 6A, a 16A and two 40A (one for the EV and one for the office that runs off this fuse box). For clarity, the supply is:
I need to replace the old fuse box in the garage with a CU and at the same time install a load balancing a fast charge outlet for electric vehicle.
Current installation has a sub panel in the house (40A) with type B MCBs: 20A for kitchen sockets and 32A for the garage supply. Main board is double RCD 80A/ 63A and DNO fuse is 100A.
10mm SWA cable underground to garage, approx 15m.
Plan is to move the kitchen sockets on to the main board (there is a spare), replace the adjacent garage sub panel for a 63A RCD panel with a 50A MCB, and replace the old fuse box in the garage with similar panel but with a 6A, a 16A and two 40A (one for the EV and one for the office that runs off this fuse box). For clarity, the supply is:
- DNO
- 100A fuse
- single rate meter (hopefully to be replaced with a smart meter ASAP)
- Henley block
- from Henley block to main CU (100A SVMS) with two RCDs: one 80A 30mA and one 63A 30mA.
- also from Henley block currently has second feed to sub panel with 40A 30mA RCD and two MCBs one B20 for kitchen sockets which I’ll move to main board spare, and one B32 feeding 10mm SWA cable to garage. This sub panel I’ll have to change as its only 40A rated.
- garage has old fuse-wire box from which are taken a lighting circuit, a ring and a second SWA that goes the to office.