To the boss on the soil stack? Certainly overly long for an unvented 40mm or 50mm pipe .... Standards are 3m @ 40mm and 4m@50mm on an unvented run.
So if you can't shorten the run by say extending a stack branch then you would ideally look to increase the size and definitely vent the run or you are in real danger of the trap getting pulled (self syphoning). Is that the only outlet on the run?