Armoured Cable Size

Joined
11 Jun 2006
Messages
121
Reaction score
0
Location
Cheshire
Country
United Kingdom
Hello

What size armoured cable will I need to run about 150m and what would the maximum load it could take be. I will be using an electrician but I am just looking at the options and pricing the work up.

Thanks

Barnman
 
You size the cable on the load you need to draw, not the other way around!

Edit: well too slow.
 
Half that - but that will mean 16mm² (no 12.5) - but then you can have 6.3kW, 27A.

Before anyone says this is way over the volt-drop limit for lighting, does it matter?
 
That would be nice but as it is a stable with a couple of storage rooms etc I will live with the limitations depending on the cost. It will need lighting, maybe a kettle, maybe a heater but I think 6.3KW will be more than enough. If I ran 10mm cable, this would save about £200 but what load would this take? Any lower I imagine I will be restricted to lights only.
 