Good Morning All,
Im wondering if anyone may be able to help or advise please.
I have an issue I believe is tied to a leak coming from the combi boiler (Biasi Riva Plus HE M296 28SMC, 2015 Model):
Last night the RCD on my home electrical system consumer unit tripped, after much hunting, unplugging and isolating, we discovered that it was tripping as soon as there was a demand from the boiler (hot water and central heating demand). We tested this and can consistently induce the fault by either having the hot tap on or having the central heating make a demand.
I removed the cover to take a look if there was anything obvious. Sure enough, on top of the pump itself, coming from Item Number 26 on the diagram, the grey capped "automatic air purger valve". There was a small but consistent weep - Id estimate one drip per 30 seconds-ish.
Furthermore the immediate area was coated in a limescale type crud - evidence that it had been like this for a while. Is water meant to come out of this valve? I have attached an image to help illustrate. I had wiped most of the water away but if you look carefully you can see the first couple of drips below the grey cap just off to the left slightly.
How and why this weep could cause a short and trip the RCD is the query - the most obvious possibility is that it sits on top of the pump unit itself and the water has seeped into the pump itself, onto the electrical gubbins within - this would do it I suppose? Perhaps its as a result of a demand being made , the pump energising causing the subsequent short?
Course of action : 1.stop the leak 2.dry out the pump 3.reassemble and try again?
Question 1: Automatic air purger valve - is it meant to remain open all the time for normal operation?
Question 2:Automatic air purger valve - Is there meant to be water coming out of it
Question 3:Automatic air purger valve - replace the whole assembly or change seals?
Question 4: Pump itself - if it has seen water inside , is it salvageable/repairable?
Any directions, tips or words of warning before I get in and about this?
I really appreciate and welcome comments or advice - thank you very much all.
Adam
Im wondering if anyone may be able to help or advise please.
I have an issue I believe is tied to a leak coming from the combi boiler (Biasi Riva Plus HE M296 28SMC, 2015 Model):
Last night the RCD on my home electrical system consumer unit tripped, after much hunting, unplugging and isolating, we discovered that it was tripping as soon as there was a demand from the boiler (hot water and central heating demand). We tested this and can consistently induce the fault by either having the hot tap on or having the central heating make a demand.
I removed the cover to take a look if there was anything obvious. Sure enough, on top of the pump itself, coming from Item Number 26 on the diagram, the grey capped "automatic air purger valve". There was a small but consistent weep - Id estimate one drip per 30 seconds-ish.
Furthermore the immediate area was coated in a limescale type crud - evidence that it had been like this for a while. Is water meant to come out of this valve? I have attached an image to help illustrate. I had wiped most of the water away but if you look carefully you can see the first couple of drips below the grey cap just off to the left slightly.
How and why this weep could cause a short and trip the RCD is the query - the most obvious possibility is that it sits on top of the pump unit itself and the water has seeped into the pump itself, onto the electrical gubbins within - this would do it I suppose? Perhaps its as a result of a demand being made , the pump energising causing the subsequent short?
Course of action : 1.stop the leak 2.dry out the pump 3.reassemble and try again?
Question 1: Automatic air purger valve - is it meant to remain open all the time for normal operation?
Question 2:Automatic air purger valve - Is there meant to be water coming out of it
Question 3:Automatic air purger valve - replace the whole assembly or change seals?
Question 4: Pump itself - if it has seen water inside , is it salvageable/repairable?
Any directions, tips or words of warning before I get in and about this?
I really appreciate and welcome comments or advice - thank you very much all.
Adam