Building regs H 2015 says WC branch pipe can have a slope of 18-90mm/m (page 9) which works out as ~1 deg to ~5 deg. Floplast, for example, do stack connections at 87.5 deg (-2.5deg) and 67.5 deg (-22.5) and 45 (-45 deg). Only the first of those meets the regs H so what am I missing? Or can I only legally use the 87.5deg part?
On a similar note, floplast have an external air admittance valve but regs H does not allow external air valves. Is there some addendum to regs H I've missed?
On a similar note, floplast have an external air admittance valve but regs H does not allow external air valves. Is there some addendum to regs H I've missed?