Building regulations for wall return on porch

Joined
16 Sep 2019
Messages
21
Reaction score
0
Country
United Kingdom
Hi,
I'm currently mid-build on a 1.6m deep x 2.8m wide porch. I've been told by the builders that I can't put the door where I want to (very close to one edge) because building regs require a >600mm return. Something to do with making sure the wall doesn't get blown over. We live near London so low wind risk.

I've been lead to believe that if a structural engineer can provide calculations to support a smaller return that it should be accepted by the building inspector. Can anybody tell me if that is true and what the likely result would be (we're hoping for ~400mm return external with a 300mm cavity wall)?

Cheers
 
You do not need Building Regulations approval for a porch, so you can have the return any size you like.

It is true that calculations can usually show that a smaller return is acceptable when considering wind load.

However, bear in mind that doors are heavy, and a slamming door can put considerable force on a narrow return; I'd be dubious about any return supporting a door being less than 2-bricks (450-ish) wide.
 
You do not need Building Regulations approval for a porch, so you can have the return any size you like.

I suppose it could be a porch open to the house....if that's still called a porch?
 
Something to do with making sure the wall doesn't get blown over

3 bricks = 675mm is often a rule of thumb as the min for a wall to act as a buttress against wind load.

You can have it as small as you like if you put in a steel post - usually cast into the founds or bolted to them.
Mind you, seems a bit overkill for a porch.

Is there a bigger return the other side - if there is, a steel across the top strapped in place would link them together.
 
I suppose it could be a porch open to the house....if that's still called a porch?
I think once you take the front door off (or replace it with an internal-grade door) it becomes an extension to the house and building regs then apply.
 
Yes, new front door so building regs apply (doing it now saves the hassle getting retrospective signoff to sell in the future), it is also >3m² so is past permitted development and required planning (part of a larger project from previous owners).

Mind you, seems a bit overkill for a porch.
I get there is a reason for the rules but it does seem overkill I agree, especially for such a small area wall and single story. Seems like this is not scenario that the rule is designed for, there should be a loophole!

The door has sidelight so will be total 1300mm wide leaving a decent return on the far side. Sadly it sounds like this inspector is a bit of a stickler so I am just going to have to go with the rules *sigh* (don't want to pause the build to get calculations done for a windpost). Perhaps we will try and get some extra space back inside by using thinner blocks for the inner skin.

Cheers for the input folks.
 
If there is 'a decent' return on the other side; and if the door is hinged at the decent return; and if you can connect the two brickwork returns with a suitable beam, the inspector might let you get away with a smaller return.
This is because the wind load is then 'shared' by the two brickwork returns.
 