Hi there. [I'm new to combi boiler problems, so I might not be explaining myself correctly.]
Over the past three weeks I've started losing central heating pressure. Starting from 2.0 bar, it drops to 0.5 bar over 24 hours.
I've checked the radiators and all seems okay. I know that everyone will say I've a leak, but I'm desperate to rule out all other causes before I have to rip up the hardwood flooring.
I've had a bag tied tightly to the PRV outlet pipe outside for two weeks and no water has collected.
To see if the domestic hot water was reducing central heating pressure, I tried the following:
Boiler: Ideal Logic Combi 30
Preheat: off
Tap Temperature: 2/3 anticlockwise
Radiator Temperature: e=economy
Function: Tap only
1. Central heating gauge = 0.6 bar
2. Run hot tap for 30 seconds, central heating gauge immediately jumps to 0.95 bar
3. After tap has closed, boiler rumbles for 60 seconds, then central heating gauge drops back to 0.6 bar
4. Steps 1 to 3 repeated 10 times, pressure always returns to 0.6 bar
Although the central heating pressure didn't drop any further, is it normal for the central heating gauge to jump to 0.95 bar when Function is set to Tap only?
I thought the central heating and domestic hot water were separate circuits, so it seems strange the pressure jumps at all.
Looking at the combi boiler instructions, this model only has a single heat exchanger so a diverter valve is needed to keep the water circuits separate.
If my steps aren't telling me anything, is there any other way I can rule out problems with the diverter valve or a leak in the exchanger?
Thanks.
Over the past three weeks I've started losing central heating pressure. Starting from 2.0 bar, it drops to 0.5 bar over 24 hours.
I've checked the radiators and all seems okay. I know that everyone will say I've a leak, but I'm desperate to rule out all other causes before I have to rip up the hardwood flooring.
I've had a bag tied tightly to the PRV outlet pipe outside for two weeks and no water has collected.
To see if the domestic hot water was reducing central heating pressure, I tried the following:
Boiler: Ideal Logic Combi 30
Preheat: off
Tap Temperature: 2/3 anticlockwise
Radiator Temperature: e=economy
Function: Tap only
1. Central heating gauge = 0.6 bar
2. Run hot tap for 30 seconds, central heating gauge immediately jumps to 0.95 bar
3. After tap has closed, boiler rumbles for 60 seconds, then central heating gauge drops back to 0.6 bar
4. Steps 1 to 3 repeated 10 times, pressure always returns to 0.6 bar
Although the central heating pressure didn't drop any further, is it normal for the central heating gauge to jump to 0.95 bar when Function is set to Tap only?
I thought the central heating and domestic hot water were separate circuits, so it seems strange the pressure jumps at all.
Looking at the combi boiler instructions, this model only has a single heat exchanger so a diverter valve is needed to keep the water circuits separate.
If my steps aren't telling me anything, is there any other way I can rule out problems with the diverter valve or a leak in the exchanger?
Thanks.