I'm trying to get my head around setting up a Euro 46 to do area set.

The scenario is a small factory that has decided to sub-let the upstairs of an office block. These will share a common lobby area.

I need to reconfigure the panel such that the tenants can only unset/set the sensors in their space (hence leaving the main factory set) but the factory staff and unset all the zones.

The bit I don't get is.... If the tenant unsets the panel & then the factory staff arrive later...... what triggers the second entry/exit to cause them to enter a code to unset the main factory?

Also, the EURO46 has areas 0, 1, A, B, C D. Whatis the difference between areas 0 & 1 and A, B, C, D?

Thanks in advanced for your help - I've installed many a panel in the past but this is the first time I've need to configure one for anything other than full set!

Adrian
 
So you will program office as area A and issue a code programmed for A only, warehouse as area B and code programmed for B only. The common lobby zones will go in A and B but under zone attributes change input areas from 'any' to 'all' so these will only be armed if both areas are set. With regards to entry tones, you could program the door to the office and the warehouse as final exit this would remind the staff to turn the system off if they are the first ones to enter there area. U will also need to turn level set off in site options
 