So was doing a little paper excessive to keep by brain active. If you had:
A) A single oven rated 3.5Kw (i.e. Steam oven)
and
B) A second single oven rated at 3.0Kw (i.e. Microwave combi oven)
That would give you a current rating of 11.56A for the first oven and 10.91A for the second oven once diversity had been taken into account right? (Domestic household and no socket)
(10A + 30% remaining current + 5A for socket outlet if applicable) for each appliance.
Now the catch is each oven's manual stipulates that it must only be fed from a OCPD of a maximum rating of 20A.
Now if I have done the diversity calcs correct, the current with the diversity taken into account would be 22.48A - Roughly 2.5A over the maximum OCPD that can be used, meaning the ovens would effectively have to be on their own circuit from the CU.
Have I got this all correct?
Regards: Elliott