Hi
I have a cpl of question, but I'm also posting as this might help others trying to get Drayton Wiser to work properly with Vaillant (or other boilers).
Setup: ecotec plus 418, S plan, installing Drayton Wiser smart controls (currently 3 rad valves).
Problem: the boiler is short-cycling sporadically... it often comes on for a very short time (as short as 10 sec!).
After a lot of testing (and help from support) this is what I worked out:
The Wiser controller operates on 6 cycles/hour max (for a gas boiler; this is also the default on evohome, so seems standard).
The Vaillant Ecotec 418 has a default anti-cycle time which (at my flow temp) seems to clock around 8/9 minutes.
So, for example: Wiser requests heat (using TPI algorithms) for 5 minutes... at minute 5, demand switches off, boiler off and starts anti-cycling for 8 mins... so when Wiser starts the next cycle (from minute 10), for the first 3 minutes of demand the boiler stays off cos it's still anti-cycling. By the time the boiler fires, the demand turns off.
I know there are some Vaillant experts here...
Is the default anti-cycle time on the ecotec plus unusually long? (the d2 setting, according to other threads)
Can this be safely (for boiler life!) reduced to say half the current setting?
Is 6 cycles/hour acceptable for this boiler?
Or is there a 'minimum boiler on' time I can set (without interfering with HW safety cut-out) to avoid the extreme short cycles?
thank you!
I have a cpl of question, but I'm also posting as this might help others trying to get Drayton Wiser to work properly with Vaillant (or other boilers).
Setup: ecotec plus 418, S plan, installing Drayton Wiser smart controls (currently 3 rad valves).
Problem: the boiler is short-cycling sporadically... it often comes on for a very short time (as short as 10 sec!).
After a lot of testing (and help from support) this is what I worked out:
The Wiser controller operates on 6 cycles/hour max (for a gas boiler; this is also the default on evohome, so seems standard).
The Vaillant Ecotec 418 has a default anti-cycle time which (at my flow temp) seems to clock around 8/9 minutes.
So, for example: Wiser requests heat (using TPI algorithms) for 5 minutes... at minute 5, demand switches off, boiler off and starts anti-cycling for 8 mins... so when Wiser starts the next cycle (from minute 10), for the first 3 minutes of demand the boiler stays off cos it's still anti-cycling. By the time the boiler fires, the demand turns off.
I know there are some Vaillant experts here...
Is the default anti-cycle time on the ecotec plus unusually long? (the d2 setting, according to other threads)
Can this be safely (for boiler life!) reduced to say half the current setting?
Is 6 cycles/hour acceptable for this boiler?
Or is there a 'minimum boiler on' time I can set (without interfering with HW safety cut-out) to avoid the extreme short cycles?
thank you!