I've just had a new boiler installed (Ideal Logic, regular boiler for system with sealed hot water cylinder). The boiler company provided a Hive unit, and I had to get someone else in to install it. However, they seem to have done it the wrong way around:
- when I select Hot Water, the boiler switches on, and the radiators get hot
- when I select Central Heating, the boiler switches on, but the radiators don't.
- when both are off, everything shuts down appropriately.
I've had a look at the wiring (after browsing a number of posts in this forum), and there's a single wire to each of terminal 3 and 4, with a bunch to L. Could it be that the electrician has just switched the wires around when connecting the two ON wires? Can I just switch these around? At the moment, I'm using the Hive the wrong way around - setting the schedule for HW and CH the way I want it for CH and HW, respectively. Obviously, I'd prefer this to work properly, though!
- when I select Hot Water, the boiler switches on, and the radiators get hot
- when I select Central Heating, the boiler switches on, but the radiators don't.
- when both are off, everything shuts down appropriately.
I've had a look at the wiring (after browsing a number of posts in this forum), and there's a single wire to each of terminal 3 and 4, with a bunch to L. Could it be that the electrician has just switched the wires around when connecting the two ON wires? Can I just switch these around? At the moment, I'm using the Hive the wrong way around - setting the schedule for HW and CH the way I want it for CH and HW, respectively. Obviously, I'd prefer this to work properly, though!