Earth fault loop impedance 3x230 nett

Joined
26 Apr 2015
Messages
51
Reaction score
0
Country
United Kingdom
How do earth fault loop impedance requirements and disconnect times change when the live to earth voltage is 133 instead of 230?

Thanks!
 
You will need a lower phase/earth impedance to ensure a sufficient current to operate the device in the required time.
 