Can an Earth wire block (4 way) be screwed directly to the side of a first floor joist under the floor boards or does it need to be first placed in a protective box.
Ans YESwhy do you want to hide it?
Is it for bathroom supplementary bonding?
Connect to what?Closest place to connect earth wire
The electric shower will be earthed to the cold water pipe and the 16mm shower grey twin and earth taken back directly to the consumer board with its own 30ma breaker when the new one is installed.If it is possible to get all the conductors to a single point then a junction (box) isn't necessary, is it?
I suspect the correct method of bonding is not being implemented.
No it won't - that's not earthing.The electric shower will be earthed to the cold water pipe
But why there?The basin, pan, bidet H & C water as fitted as required to each and C.H & radiator copper pipes all have under earth tags fitted and that cable is then routed under the studded partition into the landing floor
If you use screwed connections they have to be accessible.under the T&G flooring
But why? Why connect all the bathrooms together? Why take the bonding (not earthing) conductors out of each bathroom in the first place?There are in total three bathrooms each Earth bonded and hence there are three independent Earth cables routed the same into the landing floor
Why do you want to connect the bonding cables to one of those?so connecting three cables into one 4 way block then allows another single earth wire to be connected to one of the junction box Earth terminals.
Earthing conductors must be.I understand that such Earth cables must not be taken back direct to a consumer box.
No it won't - that's not earthing.The electric shower will be earthed to the cold water pipe
A -Inside the electric Mira shower their earth is pre-fitted connected to the CW 15mm copper supply pipe connection, they then route it into the main choc bloc Earth, that earth is then the 16mm earth cable taken back to the consumer board via breaker.
But why there?The basin, pan, bidet H & C water as fitted as required to each and C.H & radiator copper pipes all have under earth tags fitted and that cable is then routed under the studded partition into the landing floor
Why not simply connect them together where they are?
A - are you saying that these earth wires should not be connected into the earth terminal of say a junction box earth terminal that is part of another power circuit, just leave them unconnected to act as equipotential earth cables, i.e. not connected at all to any earthed power connection or junction box
If you use screwed connections they have to be accessible.under the T&G flooring
A - if those three earths cables are then fitted into an earth block but not into any circuit earth terminal are you saying they still have to be accessible, if so the only way to solve that for me is to connect another earth cable up through the studded partition into the loft for inspection and access and then should that cable be simply terminated in a box or connected to an earth terminal in say another junction box.
But why? Why connect all the bathrooms together? Why take the bonding (not earthing) conductors out of each bathroom in the first place?There are in total three bathrooms each Earth bonded and hence there are three independent Earth cables routed the same into the landing floor
A - They can still be left in each bathroom and not connected just to equal potentialise ? metalwork.
Why do you want to connect the bonding cables to one of those?so connecting three cables into one 4 way block then allows another single earth wire to be connected to one of the junction box Earth terminals.
Earthing conductors must be.I understand that such Earth cables must not be taken back direct to a consumer box.
Bonding ones don't need to be.
I don't really understand what you mean/are trying to say there. And it doesn't seem like a response to all the questions I asked and points I raised.A - So Supplimentary earth wires only connect metalwork in a bathroom connected to say metal pipework without any termination into say any junction boxes as all other electrical equipment like shaver sockets, light fittings, electrical towel rails each are earthed via their own usually flat grey twin and Earth cables into and earth cable that terminates at the consumer board ?
To summarise, please correct me as required.
1 - To connect all metalwork In a bath/shower room requires a minimum 4mm earth cable via tags to be fitted for each product connection e g metal pipe....installed but do NOT need to be connected into any power circuit/earth connection box.
The circuit protective conductors still need to be connected to the bonding.2 - All electrical products will have their own usually twin and earth cable connections to be connected into a power circuit that has its own earth connection assuming that it is not double insulated then no earth connection is necessary.
Supplementary equipotential bonding connects together extraneous-conductive-parts and the cpcs of appliances in the bathroom zones not just randomly connected to a nearby junction box that may hot have anything to do with the circuits in the bathroom.3 - so where is it necessary if needed for and Earth wire to be finally take back into the nearest power circuit earth terminal or does that not apply at all
A - YESFirstly, do you have RCD protection on ALL the circuits which supply the bathrooms?