Would appreciate advice from an expert in earthing systems.
My installation here in Spain is (I believe) a T-T system - overhead single phase power supply, only earth is at the consumer unit. This is a very good earth, connected to about 200m of reinforcing rods in the house foundations.
However, I suspect that the neutral supply line is not grounded at all, anywhere, as there is around 60v between neutral and earth within the house. This does not present much of a practical problem, but I would prefer it to be 0v!
So the question: Could/should I earth the neutral at either the consumer unit or the pylon/electricity meter (about 200m away) or both?
I am wondering if doing so might also help with nuisance tripping of the RCD during windy/stormy conditions.
Thanks