Hi,
Buying a property and was quoted £8,500 to fix the below
C1’s
• Circuit 7, socket circuit has original rubber wiring and an insulation test has a reading of under 1 meg ohm. This means the cables are seriously deteriorating and need rewiring
• Circuit 8, socket circuit has original rubber wiring and an insulation test has a reading of under 1 meg ohm. This means the cables are seriously deteriorating and need rewiring.
• Circuit 2, garage supply has been run in twin and earth cable on an overhead outside, this cable is not sufficient enough to be used outside and exposed to outside conditions. The garage wiring itself needs rewiring, cables are not clipped sufficiently and are in bad condition.
C2’S
• Circuit 1, shower circuit has original wiring. Although passing tests this cable will deteriorate very quickly and needs rewiring asap.
C3’s
• 16mm tails from meter to main switch (new standard is 25mm)
• No hard-wired smoke detectors in house
• Consumer unit is plastic (new standard is metal for fire purposes)
Estimate for work to be carried out:
To rectify code 1’s all sockets in the house need rewiring along with the garage supply and inside the garage. Total estimate for this work is £5,000
To rectify all code 2 and 3’s would include rewiring of the shower, upgrade main tails to 25mm, change the consumer unit and install smoke detectors. Total estimate for this work is £3,500
Is this a reasonable price?
Also, the estate agent sent someone over who's disputed the c1 status, saying they're actually c2s.. is this likely?
Buying a property and was quoted £8,500 to fix the below
C1’s
• Circuit 7, socket circuit has original rubber wiring and an insulation test has a reading of under 1 meg ohm. This means the cables are seriously deteriorating and need rewiring
• Circuit 8, socket circuit has original rubber wiring and an insulation test has a reading of under 1 meg ohm. This means the cables are seriously deteriorating and need rewiring.
• Circuit 2, garage supply has been run in twin and earth cable on an overhead outside, this cable is not sufficient enough to be used outside and exposed to outside conditions. The garage wiring itself needs rewiring, cables are not clipped sufficiently and are in bad condition.
C2’S
• Circuit 1, shower circuit has original wiring. Although passing tests this cable will deteriorate very quickly and needs rewiring asap.
C3’s
• 16mm tails from meter to main switch (new standard is 25mm)
• No hard-wired smoke detectors in house
• Consumer unit is plastic (new standard is metal for fire purposes)
Estimate for work to be carried out:
To rectify code 1’s all sockets in the house need rewiring along with the garage supply and inside the garage. Total estimate for this work is £5,000
To rectify all code 2 and 3’s would include rewiring of the shower, upgrade main tails to 25mm, change the consumer unit and install smoke detectors. Total estimate for this work is £3,500
Is this a reasonable price?
Also, the estate agent sent someone over who's disputed the c1 status, saying they're actually c2s.. is this likely?