A friend has a flat in Andorra. That's in Abroadland, and he's going to upgrade his supply to 10kW maximum.
Here is a list of the main electrical items:
Electric water heater (1.5kW)
Hob (2 x 500W, soon to be 4 x 500W) Assume 50% diversity, so 1kW.
Kettle (2.2kW)
Washing machine (2kW)
Microwave oven (3kW)
Lighting, TV, other entertainment stuff, computer, etc. Assume 500W.
Portable blower heater 2 x 1kW.
He wants to install an electric flow boiler, maximum demand for this is 6kW.
Clearly a combination of the heating being on, plus the kettle, washing machine, and the other paraphenalia of modern life will exceed his maximum load and, especially at breakfast time, he can predict frequent nuisance trips.
He wants to be able to turn off the heating automatically when the non-boiler loads exceed 4kW, and turn it back on when, say, the kettle has boiled and the load due to other causes drops below 4kW.
He proposes to feed the 10kW supply tails to a new fuseboard, with the electric boiler and water heater as loads (7.5kW max), then take a pair of tails from there to a second 'board with all the other loads connected. A current sensitive relay (current transformer feeding the controls of a relay) will be mounted between the first 'board and the second, set to operate at about 4kW and above (>18A), and the volt free contacts of this relay will interrupt the room thermostat's 'call for heat' signal, thus turning the heating off until the loads fall below 4kW.
He also wants a timing function to delay the switching on of the heating for a few minutes to prevent short term switching due to use of the kettle or hairdryer.
I can see that careful management of the appliances in use would mostly prevent going into an overload condition, i.e timing the water to heat before the heating switches on, delaying use of the washing machine until he goes out, etc., but occasionally the gf comes to stay. She will want the heating on, plus the telly, the hob, and the microwave, plus kettle and toaster, even an extra blower heater! If she trips the supply she'll phone him at work in a mini panic, worse still he's reluctant to show her how to reset the trip because a) it's 3 floors below in a switchroom common to the other 8 flats in the block, and b) he doesn't want to get her into the habit of regularly tripping the supply and resetting it.
Does anyone here know of an elegant way to provide the functionality he wants, without building a custom rig using RaspPi or Arduino? It would be even better if the solution includes a web based interface, so he can see how much load the gf puts on the system while he's out at work!
MM
Here is a list of the main electrical items:
Electric water heater (1.5kW)
Hob (2 x 500W, soon to be 4 x 500W) Assume 50% diversity, so 1kW.
Kettle (2.2kW)
Washing machine (2kW)
Microwave oven (3kW)
Lighting, TV, other entertainment stuff, computer, etc. Assume 500W.
Portable blower heater 2 x 1kW.
He wants to install an electric flow boiler, maximum demand for this is 6kW.
Clearly a combination of the heating being on, plus the kettle, washing machine, and the other paraphenalia of modern life will exceed his maximum load and, especially at breakfast time, he can predict frequent nuisance trips.
He wants to be able to turn off the heating automatically when the non-boiler loads exceed 4kW, and turn it back on when, say, the kettle has boiled and the load due to other causes drops below 4kW.
He proposes to feed the 10kW supply tails to a new fuseboard, with the electric boiler and water heater as loads (7.5kW max), then take a pair of tails from there to a second 'board with all the other loads connected. A current sensitive relay (current transformer feeding the controls of a relay) will be mounted between the first 'board and the second, set to operate at about 4kW and above (>18A), and the volt free contacts of this relay will interrupt the room thermostat's 'call for heat' signal, thus turning the heating off until the loads fall below 4kW.
He also wants a timing function to delay the switching on of the heating for a few minutes to prevent short term switching due to use of the kettle or hairdryer.
I can see that careful management of the appliances in use would mostly prevent going into an overload condition, i.e timing the water to heat before the heating switches on, delaying use of the washing machine until he goes out, etc., but occasionally the gf comes to stay. She will want the heating on, plus the telly, the hob, and the microwave, plus kettle and toaster, even an extra blower heater! If she trips the supply she'll phone him at work in a mini panic, worse still he's reluctant to show her how to reset the trip because a) it's 3 floors below in a switchroom common to the other 8 flats in the block, and b) he doesn't want to get her into the habit of regularly tripping the supply and resetting it.
Does anyone here know of an elegant way to provide the functionality he wants, without building a custom rig using RaspPi or Arduino? It would be even better if the solution includes a web based interface, so he can see how much load the gf puts on the system while he's out at work!
MM