Hello I'm a new poster here,
Boiler- Enviromax Combi C35 with Riello RDB Burner
The central heating has been consistently loosing pressure over time and I have sorted many leaks since moving in the house but have discovered one small leak on a radiator that looses less than 15ml of water over 24hrs. I have this leak on the to be fixed list but if I am going to drain down the system I want to fix the other issue at the same time.
this leak has been like this for some time and not affected the time the gauge takes to rise the way it does described below until now but I'm sure that's not down to the leaking radiator.
When the boiler fires for hot water I can wait some time for the boiler to produce hot water at the kitchen tap and its not that hot. Also if I repressurise the central heating circuit the pressure gauge rises like it should but if I open the filling loop tap fully open to pressurise the heating when the hot tap is running the pressure gauge does not move at all.
This leads me to think the plate heat exchanger is knackered internally as in the flow of the central heating pressure circuit is crossing through a leak internally and going either into the heat store tank via the plate heat exchanger and/or out of the hot tap which cools when the filling loop is open
The thermostatic mixing valve was replaced on the 26th of April 2017 by a plumber but it cant be turned either by the knob or with pliers on the shaft,
Do you know why its seized up after such a short period of time?
The pressure vessel is working and pressurised to the correct pressure as per instructions
Also the boiler relays click a lot when the burner is trying to light on water heating or central heating and sometimes the burner will stop after a few minutes after starting and stay off until it seems to have cooled a bit even thought the thermostat in the hall is on heating and the room temp has not risen to the set temp and the heating LED on the boiler is on
If I should replace the plate heat exchanger the Firebird manual lists a 25 plate and a 31 plate exchanger for the C35 boiler so how do I tell which one is installed in my boiler?
Thanks everyone for reading my long description
Please let me know if my diagnosis is good and I should replace the plate heat exchanger as well as fixing the radiator leak because these are really expensive for what it is and I'm running out of money to throw at this
this is my first post on here I wish id found this forum earlier
Andy
Boiler- Enviromax Combi C35 with Riello RDB Burner
The central heating has been consistently loosing pressure over time and I have sorted many leaks since moving in the house but have discovered one small leak on a radiator that looses less than 15ml of water over 24hrs. I have this leak on the to be fixed list but if I am going to drain down the system I want to fix the other issue at the same time.
this leak has been like this for some time and not affected the time the gauge takes to rise the way it does described below until now but I'm sure that's not down to the leaking radiator.
When the boiler fires for hot water I can wait some time for the boiler to produce hot water at the kitchen tap and its not that hot. Also if I repressurise the central heating circuit the pressure gauge rises like it should but if I open the filling loop tap fully open to pressurise the heating when the hot tap is running the pressure gauge does not move at all.
This leads me to think the plate heat exchanger is knackered internally as in the flow of the central heating pressure circuit is crossing through a leak internally and going either into the heat store tank via the plate heat exchanger and/or out of the hot tap which cools when the filling loop is open
The thermostatic mixing valve was replaced on the 26th of April 2017 by a plumber but it cant be turned either by the knob or with pliers on the shaft,
Do you know why its seized up after such a short period of time?
The pressure vessel is working and pressurised to the correct pressure as per instructions
Also the boiler relays click a lot when the burner is trying to light on water heating or central heating and sometimes the burner will stop after a few minutes after starting and stay off until it seems to have cooled a bit even thought the thermostat in the hall is on heating and the room temp has not risen to the set temp and the heating LED on the boiler is on
If I should replace the plate heat exchanger the Firebird manual lists a 25 plate and a 31 plate exchanger for the C35 boiler so how do I tell which one is installed in my boiler?
Thanks everyone for reading my long description
Please let me know if my diagnosis is good and I should replace the plate heat exchanger as well as fixing the radiator leak because these are really expensive for what it is and I'm running out of money to throw at this
this is my first post on here I wish id found this forum earlier
Andy