I need to put in a supply for a shed/workshop about 60m from the incoming TNS service, which appears to be fed by a dedicated (only serves this one house) pole-mounted transformer, Ze=0.23ohm. No extraneous conductive parts in the shed/workshop (wooden construction and plastic water supply).
Normally I work in the city so 60m away outbuildings are new to me.
Exporting the earth using a 3-core SWA will probably cost less than TTing (after concreting in an earth pit and whatnot, despite the cheaper and lighter 2-core cable) and mean lower EFLI's, so that would be my preferred option.
I have just received a copy of GN8 but flicking through it doesn't seem to give much/any guidance on when a TT supply is preferred over using the distributors facility. My understanding is that the only issue would be if the earth potential at the workshop is significantly different to the suppliers earth potential, is this correct? and is it possible to test the difference in earth potential over 60m? (how?)
The workshop is on the other side of a small valley and stream to the house/incoming service.
Any thoughts?
Thanks
Normally I work in the city so 60m away outbuildings are new to me.
Exporting the earth using a 3-core SWA will probably cost less than TTing (after concreting in an earth pit and whatnot, despite the cheaper and lighter 2-core cable) and mean lower EFLI's, so that would be my preferred option.
I have just received a copy of GN8 but flicking through it doesn't seem to give much/any guidance on when a TT supply is preferred over using the distributors facility. My understanding is that the only issue would be if the earth potential at the workshop is significantly different to the suppliers earth potential, is this correct? and is it possible to test the difference in earth potential over 60m? (how?)
The workshop is on the other side of a small valley and stream to the house/incoming service.
Any thoughts?
Thanks