The load current in any part of the circuit should be unlikely to exceed for long periods the current-carrying capacity of the cable (Regulation 433.1.5 refers). This can generally be achieved by: (iv) taking account of the total floor area being served. (Historically, a limit of 100 m² has been adopted.)
(i) Low voltage installations supplied directly from a public low voltage distribution system | 3% | 5% |
(a) Type B circuit-breakers to BS EN 60898 and the overcurrent characteristics of RCBOs to BS EN 61009 rating (amperes) 32 ZS (ohms) 1.38
These are the bits we are looking at, so we assume 20 amp centre of ring final and 12 amp even spread, so Design current for circuit Ib = 26 amps, so the line - neutral can increase by 0.59 Ω and the line - earth needs to be over 1.38 Ω.
It is not so cut and dried, as the 26 amp is not written in stone, however one can't simply add to a ring final, without considering the volt drop etc.
Today there is little equipment which will have a problem with volt drop, and the earth loop impedance with RCD/RCBO protection is not so important, as long as over 300 Ω then considered stable. But still, the line - neutral needs to be under 1.38 Ω for the magnetic part of the overload to work within the required time.
The MCB/RCBO is 2 or 3 devices in one, there is a thermal part which can take ½ hour or more to trip with over current, and the magnetic part which will take a fraction of a second to trip, so the circuit needs to be designed, so a short circuit will cause enough current to flow to trip the magnetic side, typically a type B needs 5 times the thermal current settings, plus 5% to allow for volt drop.
The problem DIY wise is the cheap (£40) plug in testers are designed for radials not ring finals, so are set to around 1.8 Ω not 1.38 Ω so it needs the expensive (£200) tester to work with ring finals.