Hello everyone, hope you are all good.
I’m having a problem extending the horizontal flue.
I have built an extension and want to extend the horizontal flue by 4m. The boiler is a Baxi NetaTec 33GA and in the specs it says a 60/100 flue length up to 10m with a deduction of 1m per 93 degree bend and 0.5m per 135 degree bend
My calculation is 4m tube, 1x93. 2x135 = 6m which is well within tolerance.
My problem is when I connect the 93 degree to the boiler then 0.5m extension through the wall, then 2 135 degree bends it all works, steam is coming out and hot water works. As soon as I put the first 1m extension onto this the boiler stops working, the water goes up to 39degrees and back down and will never go past 39.
Does anyone have any advise please?
I’m having a problem extending the horizontal flue.
I have built an extension and want to extend the horizontal flue by 4m. The boiler is a Baxi NetaTec 33GA and in the specs it says a 60/100 flue length up to 10m with a deduction of 1m per 93 degree bend and 0.5m per 135 degree bend
My calculation is 4m tube, 1x93. 2x135 = 6m which is well within tolerance.
My problem is when I connect the 93 degree to the boiler then 0.5m extension through the wall, then 2 135 degree bends it all works, steam is coming out and hot water works. As soon as I put the first 1m extension onto this the boiler stops working, the water goes up to 39degrees and back down and will never go past 39.