G2-12 Alarm Bell Wiring

Joined
15 Apr 2015
Messages
38
Reaction score
0
Location
Westmorland
Country
United Kingdom
Hi all,

I'm hoping someone can help me. I've recently installed a Honeywell G2-12 into my home.
I've installed all the sensors and everything was working fine.

Lastly I needed to wire the internal sounder (i've decided I don't require ta bell box at the moment). Whilst installing the internal sounder I seem to have created a fault: Bell Fuse, which I can't clear through panel reset.

I checked all the fuses and they seem fine, and have removed the bell wiring.

Can someone help me:

1. Diagnose / clear the bell fuse alert
2. Advise the correct installation of the internal sounder.

Some pictures to help my description:



Thank you
Vin
 

Attachments

  • IMG_7569 2.jpg
    IMG_7569 2.jpg
    216.1 KB · Views: 295
  • IMG_7571.jpg
    IMG_7571.jpg
    385.8 KB · Views: 280
  • IMG_7576.jpg
    IMG_7576.jpg
    294 KB · Views: 289
F3 is the bell fuse , have you tested it using a multi meter?

A member called galaxyguy is the expert on these systems , I'm sure he will be along soon to help
 
I didn’t as I left my multimeter at home. I will check tomorrow. I hope galaxy guy gets in contact. Thanks for your reply. Vin
 
Hi, it's likely you've blown the fuse.

A plain 12v Sounders can be connected with the positive going to +12v supply terminal and the negative going to the bell output (symbol of a bell on the PCB). You will also need a wire link between the tamper return T and 0V.
 
Hi, it's likely you've blown the fuse.

A plain 12v Sounders can be connected with the positive going to +12v supply terminal and the negative going to the bell output (symbol of a bell on the PCB). You will also need a wire link between the tamper return T and 0V.

Hi GalaxyGuy,

Yes i’ve just checked the fuse using a multimeter as per sircerebus666 and it is blown.
So I just need to connect +ve and -ve as you’ve described, will i also need to change any settings to be -ve/+ve trigger?

Thanks
Vin
 
No, the settings will remain the same. In default settings, the trigger output will be pulled to ground and that activates the sounder.
 
Hi,

Okay i’ll try that. My bell has an internal battery. Originally i connected H+ to 12v bell
H- to 0V
R- to bell
Bridge T to 0V

This blew the fuse, although not sure it blew the fuse because i did it in engineering mode with power still to the panel.

Does what I originally did sound correct?

Thanks
Vin
 
Yes, that wiring is correct. You may have shorted something and blown the fuse if connecting while the power was on.
 
Yes, that wiring is correct. You may have shorted something and blown the fuse if connecting while the power was on.

Hi GalaxyGuy,

Just wanted to let you know, I took your advice. Replacing the fuse and wiring as you instructed solved the issue.

Thanks you
 
Yes, that wiring is correct. You may have shorted something and blown the fuse if connecting while the power was on.

Hi,

Is anyone able to offer advice on the flowing:

I set the alarm using
Code:
 + A when leaving
When entering I used [code] + Ent but the alarm doesn’t unset. Instead i get the message “Status Set”.

What is the correct way to set/unset the system?
 
The defaults for this system are to unset using a prox tag. This is based on requirements for police response. If the system is not monitored and you want to unset from full set using the code, you need to change the DD243 restrict keypad option in menu 51.55.3 - Set to 0 (No)
 
The defaults for this system are to unset using a prox tag. This is based on requirements for police response. If the system is not monitored and you want to unset from full set using the code, you need to change the DD243 restrict keypad option in menu 51.55.3 - Set to 0 (No)

Hi GalaxyGuy,
I also have prox keys, but they didn’t seem to work to set/unset. I added the serial numbers manaully via Users menu option.

Thanks
 
The serial number is for the standlone MAX reader only, not the Keyprox keypads. You'll need to add the fobs by pressing 1 and A together briefly when in the "Card No" menu for the user. Erase the existing serial number first.
 
The defaults for this system are to unset using a prox tag. This is based on requirements for police response. If the system is not monitored and you want to unset from full set using the code, you need to change the DD243 restrict keypad option in menu 51.55.3 - Set to 0 (No)

Thanks GalaxyGuy your advice is spot on as always. I’m up and running with ProxKey tags
 
The defaults for this system are to unset using a prox tag. This is based on requirements for police response. If the system is not monitored and you want to unset from full set using the code, you need to change the DD243 restrict keypad option in menu 51.55.3 - Set to 0 (No)

Thanks GalaxyGuy your advice is spot on as always
 
Back
Top