I want to wire a recently acquired summerhouse. I have a detached study which has a sub cu with plenty of free slots on both the non-rcd and the rcd sides. I propose to run 4mm2 cable a distance of 18 metres from the sub cu in the study to the summerhouse. i will protect the circuit with a 20 A mcb. The circuit will consist of 3 double sockets and a spur from one of the sockets (fused down to 3A) for a couple of lights.
If I place the 20A mcb on the rcd side of the sub cu will this give me the required protection? I realise that if the rcd activates i will also lose the light in the summerhouse. Should I run two cables from the sub cu - one 4mm2 for the sockets on a 20A mcb on the rcd side of the sub cu and the other a 2.5mm2 cable for the summerhouse lights protected by a 10A mcb on the non-rcd side of the sub cu in the study.
I also realise that where these cables are outside they must be SWA and buried etc. can these SWA cables be connected directly at the sub cu or would I be better off bringing ordinary 4mm2 T&E from the sub cu and connecting to the SWA using the appropriate type of metal box on the outside of the study wall.
At the summerhouse end how do I terminate the 4mm2 SWA and join to 2.5mm2 T&E for sockets.
Please note i am in the Rep. of Ireland where P regulations do not apply.
Any thoughts would be appreciated.
Thanks
I want to wire a recently acquired summerhouse. I have a detached study which has a sub cu with plenty of free slots on both the non-rcd and the rcd sides. I propose to run 4mm2 cable a distance of 18 metres from the sub cu in the study to the summerhouse. i will protect the circuit with a 20 A mcb. The circuit will consist of 3 double sockets and a spur from one of the sockets (fused down to 3A) for a couple of lights.
If I place the 20A mcb on the rcd side of the sub cu will this give me the required protection? I realise that if the rcd activates i will also lose the light in the summerhouse. Should I run two cables from the sub cu - one 4mm2 for the sockets on a 20A mcb on the rcd side of the sub cu and the other a 2.5mm2 cable for the summerhouse lights protected by a 10A mcb on the non-rcd side of the sub cu in the study.
I also realise that where these cables are outside they must be SWA and buried etc. can these SWA cables be connected directly at the sub cu or would I be better off bringing ordinary 4mm2 T&E from the sub cu and connecting to the SWA using the appropriate type of metal box on the outside of the study wall.
At the summerhouse end how do I terminate the 4mm2 SWA and join to 2.5mm2 T&E for sockets.
Please note i am in the Rep. of Ireland where P regulations do not apply.
Any thoughts would be appreciated.