Gas boiler cupboard - Safety

Joined
16 Mar 2014
Messages
71
Reaction score
5
Location
Devon
Country
United Kingdom
I'm looking to create a cupboard around my kitchen combi boiler.
Is it safe to cover all 5 sides? Or do the top or bottom have to be left exposed?

Also, is there any issue in trying to line the cupboard with some sort of soundproofing material?

Thanks for any input.
 
1. Check the installation manual for your boiler make and model for required clearances, both installation clearances and servicing clearances.
2. Nothing wrong with soundproofing provided:
2a. It is not flammable material.
2b. You allow for manufacturer's required installation / servicing clearances when installing it.
 
I understand you can completely enclose them, but check the manual for essential clearances. My cupboard is to manufacturers spec., but in addition I made it open at the top and made it quickly removable for all-round access anyway.
 
Looking at this, it looks like I could cover it on all sides?

upload_2022-2-11_21-4-4.png


upload_2022-2-11_21-5-11.png
 

Attachments

  • upload_2022-2-11_21-3-52.png
    upload_2022-2-11_21-3-52.png
    32.7 KB · Views: 67
Casings round boilers are often a massive pita even if they confirm to mi's.
As above at the very least make it easily removable.
 
Air flow to help keep the appliance cool, access for servicing and a leak does not wreck the cupboard.
Assuming it is room sealed as most are these days.(y)
 
Air flow to help keep the appliance cool, access for servicing and a leak does not wreck the cupboard.
Assuming it is room sealed as most are these days.(y)
and new boilers do not need air for cooling which is why you go by minimum dimensions which allows for servicing etc (y)
 
Jus for reference, Viessmann got back to me and said:

"5mm either side of the boiler, 150mm below and 250mm above the boiler.
With the cupboard door open 700mm in front of the boiler."
 