I'll be building a ground floor shower room. It won't be a wet room, but the tray will be directly on the floor. (Concrete, early 1970's, no insulation)
The 90mm wide shower trap has pipe invert at about 70mm. Allowing 18mm/M fall, I'll need to dig down to ~ 110mm below ex floor at the point where the waste exits the wall to join the stack. (That's still above external ground level).
The screed will be only ~50 max (not yet dug any up). Assuming for now that the DPM is below the screed (not yet found that out), I'll need to penetrate the DPM and cut into concrete for the waste pipe. (I'd be fairly sure there will be no steel in the site concrete).
What's going to be the best way to repair the DPM and to seal it round the pipe? I'm thinking I'll need to remove a wider strip of the screed in order to expose more polythene have something to tape to. I have a concept that I'd create a smoothed trough with some new adhesive mortar (so as not to puncture new polythene) and line it with a DPM taped on. Only I'm not keen of relying on sticky tape. Are there better solutions?
The job is under Building control, so I'm sure the inspector will like a nice solution as well!
The shower can't be lifted higher (elderly person).
The 90mm wide shower trap has pipe invert at about 70mm. Allowing 18mm/M fall, I'll need to dig down to ~ 110mm below ex floor at the point where the waste exits the wall to join the stack. (That's still above external ground level).
The screed will be only ~50 max (not yet dug any up). Assuming for now that the DPM is below the screed (not yet found that out), I'll need to penetrate the DPM and cut into concrete for the waste pipe. (I'd be fairly sure there will be no steel in the site concrete).
What's going to be the best way to repair the DPM and to seal it round the pipe? I'm thinking I'll need to remove a wider strip of the screed in order to expose more polythene have something to tape to. I have a concept that I'd create a smoothed trough with some new adhesive mortar (so as not to puncture new polythene) and line it with a DPM taped on. Only I'm not keen of relying on sticky tape. Are there better solutions?
The job is under Building control, so I'm sure the inspector will like a nice solution as well!
The shower can't be lifted higher (elderly person).