Help with small leak from boiler end cap hot water pipe

Joined
10 Sep 2019
Messages
4
Reaction score
0
Country
United Kingdom
Hi,

Have used this forum a lot recently but this is my first post as i don't want something small to turn into a bog problem.

Hoping someone can help me identify and rectify what needs doing, i have just moved into a new house and the boiler seems fairly new its a combi boiler and worcester bosch,

i noticed a small leak from a pipe i have attached the images and circled the pipe.

this pipe gets hot when the hot water runs and the end cap moved up and down the pipe, i tried to tighten but it just spun freely i can push it in and it just pops back out im guessing its not supposed to do that.

how would i tighten it or stop the small leak, if i have to fit a new cap do i have to drain the system, i'm happy to cover it in flux and heat it with it in situ if that's a solution, I'm just concerned its going to be a major problem at some point.

Thanks in advance
 

Attachments

  • 20190919_165414.jpg
    20190919_165414.jpg
    88.6 KB · Views: 366
  • 20190919_165403.jpg
    20190919_165403.jpg
    248.8 KB · Views: 390
  • 20190919_165439.jpg
    20190919_165439.jpg
    165.5 KB · Views: 377
I have tried this and it just spins unless I'm doing some thing wrong.

I'm scared of it popping off and flooding.

Do I have to turn both?
 
I have tried this and it just spins unless I'm doing some thing wrong.

I'm scared of it popping off and flooding.

Do I have to turn both?

Its a standard compression cap.
Hold the front cap still, with a spanner and use another spanner/wrench, to turn the backnut anticlockwise WHILST LOOKING AT IT FROM THE FRONT.

Think of it as holding a bottle screw cap still, whilst turning the bottle to tighten.

It might be that there's no olive :eek: or the olive has been pinched too far towards the end of the pipe.

It could go pear shaped on you so maybe drain down and remake the fitting.

I'd have a go at tapping it backwards and tightening, but then I'd be prepared for "eventualities" ;)
 
Its a standard compression cap.
Hold the front cap still, with a spanner and use another spanner/wrench, to turn the backnut anticlockwise WHILST LOOKING AT IT FROM THE FRONT.

Think of it as holding a bottle screw cap still, whilst turning the bottle to tighten.

It might be that there's no olive :eek: or the olive has been pinched too far towards the end of the pipe.

It could go pear shaped on you so maybe drain down and remake the fitting.

I'd have a go at tapping it backwards and tightening, but then I'd be prepared for "eventualities" ;)

Thanks for that I will try this over the weekend, as you suspected I now have a nother question.

Can I isolate that pipe via the boiler green Star24i juniour mk iv or will I need to drain the whole system?

Thanks again.
 
Did this over the weekend and its all sorted thanks everyone for the help and advice
 