Hi,

recently wired up a hive to my boiler.

The receiver switches off when you turn the heating below current temperature and switches on when putting heat on or boosting.

If I leave the clock on the problem is the boiler doesnt switch on or off with the hive controls so it would stay on 24/7

any ideas where I am going wrong
Currently wired

8254FFEA-B746-4F41-A09B-63C60F09666F.jpeg A8BA61FD-CB2C-4213-BB97-1EFE8A2231A6.jpeg CE6D8D71-285E-49FC-B206-C853DED31917.jpeg
 
you need to remove the brown link between the last two terminals in your pic, then the two terminals go to 1&3 on the hive , either way round it doesnt matter, as you have linked live and 1 on the Hive try removing the link at the boiler and putting the black wire into the last terminal of the boiler with the link removed
 
Last edited:
Also, why have you used heating off terminal in the Hive? You’re not supposed to use twin and earth in a boiler either, it should be heat resistant cable, usually flex.
 
Sadly, I didnt originally install it, it was a electrician when rewiring the house.

Im just trying to sort it out as he keeps telling me its the hive reciever not his wiring.
 