Hive wiring into Worcester 28 cdi RSF

Joined
3 Jan 2019
Messages
4
Reaction score
0
Country
United Kingdom
Hi

New to this so please bare with me. Please can anyone verify the wiring of a Hive single channel reciever into a Worcester 28cdi combo boiler. I have attached a diagram of the hive connections and also the wiring for the boiler connections. Some say leave terminal 4 on the hive empty others show different and getting confused with all the conflicting info. Thanks in advance
 

Attachments

  • 9D5422AB-F7A6-48D4-B270-0A9A3456FE79.jpeg
    9D5422AB-F7A6-48D4-B270-0A9A3456FE79.jpeg
    106.5 KB · Views: 1,107
  • 0F38E7D1-801B-421A-9EE5-547714620A27.jpeg
    0F38E7D1-801B-421A-9EE5-547714620A27.jpeg
    87.2 KB · Views: 883
There are two versions of the Hive. The single channel version you have posted a photo of clearly shows terminal 4 is "unused" so don't use it. Terminal 2 won't be used either.

Boiler Ns (Neutral Supply) = Hive N

Boiler Ls (Live Supply) = Hive L

Boiler Lr (Live Return) = Hive 3 (Heating on)

A wire link is required between between Hive terminals L and 1 (Common)

If you have to open up a 'room sealed' part of your boiler to access the wiring terminals with the boiler you have, this is not a DIY job and should be done by a Gas Safe engineer who can make sure that it is properly sealed up again afterwards.
 