Hello. First time poster, happy to be torn to shreds if appropriate!
I have recently moved house and found that the room thermostat was wildly inaccurate. It was a Horstmann HRT-2.
I replaced this with a Drayton RTS-8. When I switched the heating power back on, the 3A central heating fuse blew immediately. I replaced the fuse, put the old 'stat back and everything appeared normal.
When the CH timer (Drayton Lifestyle LP522, set to turn off at 21:00) turned off, the boiler continued to fire and the room stat "calling for heat" LED remained lit. Turning the 'stat temperature down turned off the LED and shut the boiler down.
My understanding is that what should happen is (if stat isn't satisfied) - timer on, stat on, zone valve switch on, boiler on OR timer off, stat off, zone valve switch off, boiler off
I have timer off, stat on, switch on, boiler on. Removing power to the timer removes power to the stat.
The timer CH light is off so timer thinks it isn't calling for heat yet the 'stat is receiving power.
My theory is that when I replaced the thermostat I fried the timers switched live output switch and it is stuck as permanently on.
Can anyone suggest whether I'm in the right ball park? If so, I'll be buying a new timer unit and will move on to why the new stat blew the heating system fuse.
Hello. First time poster, happy to be torn to shreds if appropriate!
I have recently moved house and found that the room thermostat was wildly inaccurate. It was a Horstmann HRT-2.
I replaced this with a Drayton RTS-8. When I switched the heating power back on, the 3A central heating fuse blew immediately. I replaced the fuse, put the old 'stat back and everything appeared normal.
When the CH timer (Drayton Lifestyle LP522, set to turn off at 21:00) turned off, the boiler continued to fire and the room stat "calling for heat" LED remained lit. Turning the 'stat temperature down turned off the LED and shut the boiler down.
My understanding is that what should happen is (if stat isn't satisfied) - timer on, stat on, zone valve switch on, boiler on OR timer off, stat off, zone valve switch off, boiler off
I have timer off, stat on, switch on, boiler on. Removing power to the timer removes power to the stat.
The timer CH light is off so timer thinks it isn't calling for heat yet the 'stat is receiving power.
My theory is that when I replaced the thermostat I fried the timers switched live output switch and it is stuck as permanently on.
Can anyone suggest whether I'm in the right ball park? If so, I'll be buying a new timer unit and will move on to why the new stat blew the heating system fuse.