Installing AG6 BellBox to Accenta Mini G4 Alarm

Joined
19 Nov 2016
Messages
92
Reaction score
0
Country
United Kingdom
Hi,

I am currently installing an Intellisense AG6 bellbox to a Honeywell Accenta Mini G4 system.

I just want to double check the wiring of the bellbox.

On the Alarm control panel is have the connections:

BELL -
BELL +
STROBE -
SCB T
SCB A

On the Bell Box I have:

ST -
R -
SW -
V +
V -

How should I connect these please?

Many thanks
 
Bell + =V+
Bell - = SW-
STROBE - = ST-
SCB T = R-
SCB A = V-

Hi again,

I have wired up the bell box now exactly as you suggested.

Sorry but I now have another question.

When I power on the alarm system. 3 of my PIRs are powered on, but 1 has not power / light and is not working.

But they are all wired the same way and all the connections on both ends seem fine.

Also, during walk test 2 of the PIRs are constantly activating (showing as 1) even in an empty room.

Thanks
 
Last edited:
I had one of my PIR not working then when i checked I had changed the wires on this one thinking it was the same as the others. I hope you get it sorted.
 
I had one of my PIR not working then when i checked I had changed the wires on this one thinking it was the same as the others. I hope you get it sorted.

Hey,

Thanks, all of my PIRs are the same make/model and have all been wired the same way. However, i will double check everything again in case i've done something daft!!
 
If you have a meter check the voltage at the pir.
You could have a break in the cable so I would check continuity of the cable.
 