I agree with all that.
Whilst that is conceptually theoretically true (but see below re details), I doubt very much whether the additional socket the OP wants for 'new technology' will be asked to carry any appreciable load.
As a matter of detail, in the common situation of Method C 2.5mm² cable, it's actually about two-thirds, not one-third. In that situation, even in in the 'worst case' (32A load applied at one point on ring), the current in the short leg of the cable would only exceed it's CCC (27A) if 'the point' were within about 16% (of total ring length) from one end of the ring - hence no arrangement of loads (totalling ≤32A) within the "middle 68%" of the ring could result in more than 27A flowing in any cable.
Kind Regards, John