We had our Electrolux combi microwave/fan oven replaced with a brand new one under warranty as our old one was written of due to severe rust, what prevented a previous repair man being unable to get to and replace the heater element what was leaking current to earth and tripping the RCD.
I was working, so it was my mum who was dealing with the installation of the replacement.
However the service man who was replacing the microwave fan oven told my mum that if we are getting nuisance trips, then you should upgrade the 20A type B MCB to a 32A type B MCB.
(The tripping in the past was only even the RCD, not the MCB; I guess he could not figure that out.)
The service man surely could see the microwave fan oven was wired in 2.5mm² T&E, which surely he would have known would be unsuitable for a 32A MCB!?
Anyhow, the the 20A MCB feeds a 3.5KW steam oven and the 3Kw microwave fan oven that was replaced. (Separate cable from 20A MCB to each oven, each with there own isolator.)
So 6.5Kw / 28.26 Amps @ 230v in total.
Once you have applied diversity (10 A + 30% balance), I make it as 10A + 5.48A for a total of 15.48 Amps, what is fine for the 20A MCB.
Ok, we do have a socket on the bottom ovens isolator what is not used and tucked away behind a pull out draw, and yes the 5A diversity for that socket would take us over 20A by half a amp.
I will probably relocate the bottom ovens isolator for a dual pole 20A one at some point as it's very hard to reach at the moment.
Anyway, rant over about inappropriate advice from a appliance service tech.
Regards: Elliott.
I was working, so it was my mum who was dealing with the installation of the replacement.
However the service man who was replacing the microwave fan oven told my mum that if we are getting nuisance trips, then you should upgrade the 20A type B MCB to a 32A type B MCB.
(The tripping in the past was only even the RCD, not the MCB; I guess he could not figure that out.)
The service man surely could see the microwave fan oven was wired in 2.5mm² T&E, which surely he would have known would be unsuitable for a 32A MCB!?
Anyhow, the the 20A MCB feeds a 3.5KW steam oven and the 3Kw microwave fan oven that was replaced. (Separate cable from 20A MCB to each oven, each with there own isolator.)
So 6.5Kw / 28.26 Amps @ 230v in total.
Once you have applied diversity (10 A + 30% balance), I make it as 10A + 5.48A for a total of 15.48 Amps, what is fine for the 20A MCB.
Ok, we do have a socket on the bottom ovens isolator what is not used and tucked away behind a pull out draw, and yes the 5A diversity for that socket would take us over 20A by half a amp.
I will probably relocate the bottom ovens isolator for a dual pole 20A one at some point as it's very hard to reach at the moment.
Anyway, rant over about inappropriate advice from a appliance service tech.