First post after getting my first house.
So, I've traced the cables round and read up on the regs but I'm going round in circles with checking a few things. Do I need to get somebody in to put these things right before we start to decorate(over the next 5 years!)
I would pay for a proper inspection report, but funds are tight after piling everything into the purchase. First priorty is safety, second is not have to knock walls about in the future if a inspection report for selling(heaven forbid after the last move!) forced us to put defects right, e.g. the conduit in the walls.
I'd be grateful for any input you can give.
1) The ring circuits are in 2.5mm twin and earth with 32A RCBOs.
Is this normal for ring circuits fixed in conduit in plaster or do I need to get somebody to de-rate the RCBOs down(or worse, get the conduit removed), I've been trying to look the conduit issue up, but I'm getting confused by all the reference methods for fixing, not to mention grouping, which everyone seems to ignore anyway!
Here are the details;
2)The kitchen seems OK with a 2.5mm ring circuit to the above surface sockets, a 2.5mm radial for the fridge and freezer.
There is a 10mm supply to the oven. All seems good.
The unusual thing is the 10mm twin and earth supply to a small consumer unit fixed to the wall behind the lower cupboard.
The details are;
mini consumer unit has;
Is this mini consumer unit normal practice nowadays and are the details safe and unlikely to give defect codes in a future inspection report?
Thanks!
So, I've traced the cables round and read up on the regs but I'm going round in circles with checking a few things. Do I need to get somebody in to put these things right before we start to decorate(over the next 5 years!)
I would pay for a proper inspection report, but funds are tight after piling everything into the purchase. First priorty is safety, second is not have to knock walls about in the future if a inspection report for selling(heaven forbid after the last move!) forced us to put defects right, e.g. the conduit in the walls.
I'd be grateful for any input you can give.
1) The ring circuits are in 2.5mm twin and earth with 32A RCBOs.
Is this normal for ring circuits fixed in conduit in plaster or do I need to get somebody to de-rate the RCBOs down(or worse, get the conduit removed), I've been trying to look the conduit issue up, but I'm getting confused by all the reference methods for fixing, not to mention grouping, which everyone seems to ignore anyway!
Here are the details;
- cables are plastered into walls, often in plastic conduit(both oval and round),
- None of the cable routes in walls or above ceilings are insulated,
- The cables are grouped in a couple of plastic conduits(1 meter or so) fixed on the wall where they leave the consumer unit and also in one place where 2 of the circuits(plus a 2.5mm radial) run in an open channel on top of a steel beam.
2)The kitchen seems OK with a 2.5mm ring circuit to the above surface sockets, a 2.5mm radial for the fridge and freezer.
There is a 10mm supply to the oven. All seems good.
The unusual thing is the 10mm twin and earth supply to a small consumer unit fixed to the wall behind the lower cupboard.
The details are;
- 10mm twin and earth in oval conduit in the wall, no thermal insulation anywhere.
- fed from from a 40A mcb in the rcd side of the main split consumer unit.
- there is no back on the cupboard so the mini CU is accessible
- The 10mm cable has dp isolation and socket in the wall above the work surface before the mini consumer unit.
mini consumer unit has;
- 2 x 20A mcbs for 2 single sockets for dishwasher and washing machine
- 1 x 32A mcb for the hob outlet(isolator and socket)
Is this mini consumer unit normal practice nowadays and are the details safe and unlikely to give defect codes in a future inspection report?
Thanks!