OK so here is what I have done. Put in pipework to new rad, drained down full system, moved rad to new location on adjacent wall
Connected back up
Re filled sealed system to 1 bar cold.
From upstairs bled all rads
Re filled loop to 1 bar as many times as necessary.
Starting with moved rad bled remaining rads. Checked presure again.
Turned heating on - whole house fine except for moved rad and two others.
Checked all upstairs rad lockshields were at 1/4 turn - yup!
Checked zone valves in loft 3 of, one connected to pump one connected to HW coil in tank and one other. Flipped them all to manual - two of them had no resistance at all so assuming open already and the other one resistance was felt as I latched it open.
Checked pressure vessel with a quick press on the valve - yep thats air. Couldn't see any pipes set up to manually vent air.
If any of you kind gents have any suggestions I would love to hear from you.
Moving a rad eh? Who'd a thought it was anything but simple?
Oh and fully drained down again and carefully repeated the above and shut everyone down EXCEPT the moved rad. No joy :,-(
All help hints suggestions and advice gratefully received.
Cheers
Rob
Connected back up
Re filled sealed system to 1 bar cold.
From upstairs bled all rads
Re filled loop to 1 bar as many times as necessary.
Starting with moved rad bled remaining rads. Checked presure again.
Turned heating on - whole house fine except for moved rad and two others.
Checked all upstairs rad lockshields were at 1/4 turn - yup!
Checked zone valves in loft 3 of, one connected to pump one connected to HW coil in tank and one other. Flipped them all to manual - two of them had no resistance at all so assuming open already and the other one resistance was felt as I latched it open.
Checked pressure vessel with a quick press on the valve - yep thats air. Couldn't see any pipes set up to manually vent air.
If any of you kind gents have any suggestions I would love to hear from you.
Moving a rad eh? Who'd a thought it was anything but simple?
Oh and fully drained down again and carefully repeated the above and shut everyone down EXCEPT the moved rad. No joy :,-(
All help hints suggestions and advice gratefully received.
Cheers
Rob