Nest Thermostat E wiring to Greenstar 32CDi ERP Compact

Joined
29 Oct 2020
Messages
7
Reaction score
2
Country
United Kingdom
Hi

I have a Worcetser Bosch Greenstar boiler with wireless Comfort 1 RF thermostat control.

Please can someone help me replace this with the Nest Thermostat E?

I have attached photos of my current boiler wiring below.
IMG_20201029_101648893.jpg
IMG_20201029_101113306.jpg

Many thanks

Dan
 
The white link between terminals CH and L is removed. And assuming that you have the UK version of the Nest-e that looks like this:

145870-smart-home-review-hands-on-nest-thermostat-e-initial-review-image16-irgcqenlqw.jpg


The L terminal should be wired to Nest-e 'C'

The CH terminal should be wired to Nest-e 'NO'

The boiler's built in time / temperature control for the Central heating should be set to be permanently 'on' 25/7 otherwise it will interfere with the operation of the Nest-e
 
Last edited:
FYI I amended my first post to include:
The boiler's built in time / temperature control for the Central heating should be set to be permanently 'on' 25/7 otherwise it will interfere with the operation of the Nest-e
Just incase you missed it.
 
FYI I amended my first post to include:
Just incase you missed it.
@stem never fitted an external control to that make of Worcester but certainly on the older ones that wouldnt work, the receiver in the boiler set at constantly on will constantly look for the thermostat transmitter, on the older ones you have to remove the ribbon and the HW pre heat is also disabled , as said not totally sure if that one is the same but would suspect it is
 
Hi Ian
The 'test' doesnt turn on the heating - do you think something else needs to be disconnected?
Many thanks
Dan
 
The wireless Comfort RF is still controlling the heating....
Regards
Dan
 
@stem never fitted an external control to that make of Worcester but certainly on the older ones that wouldnt work, the receiver in the boiler set at constantly on will constantly look for the thermostat transmitter, on the older ones you have to remove the ribbon and the HW pre heat is also disabled , as said not totally sure if that one is the same but would suspect it is
Thanks @ianmcd. That's interesting, but makes we wonder why the white link between the external control terminals would be fitted if the boiler internal controls override anything connected to them. What would be the solution? removing the comfort RF?
 
Thanks @ianmcd. That's interesting, but makes we wonder why the white link between the external control terminals would be fitted if the boiler internal controls override anything connected to them. What would be the solution? removing the comfort RF?
On the older ones you just unplug the ribbon, the receiver is plugged directly into the pcb if you unplug it , you can install external controls
 
Hi Ian, Stem
I'll give it a go and let you know.
Really appreciate your efforts with this.
Dan
 