I'm upgrading my oven and hob and am looking for confirmation on my calculations. Currently it is 6mm2 wiring through the isolation switch with a 5A socket included. Outlet just under 14m from consumer unit, B40 MCB & RCD, cable running through ceiling void (some with glass fibre insulation), then into wall in PVC conduit.
New oven & hob are a higher rating. Using diversity I've calculated the following.
@ 230V
Oven: 4.9kW=21.3A
Induction hob: 7.2kW=31.3A
As 2 separate units have to split so: (10A + (11.3Ax0.3))+(10A+(21.3Ax0.3))=29.78A
This would be ok for 6mm2 cable.
However +5A socket = 34.78A which isn't. So my easiest solution without ripping out wiring etc is to change the current isolation switch so it doesn't have a socket.
Am I correct or am I missing something. Thanks for any input.
I'm upgrading my oven and hob and am looking for confirmation on my calculations. Currently it is 6mm2 wiring through the isolation switch with a 5A socket included. Outlet just under 14m from consumer unit, B40 MCB & RCD, cable running through ceiling void (some with glass fibre insulation), then into wall in PVC conduit.