That is a fairly commom arrangement and an excellent drawing.
Some will grouse about using the FCU as the everyday light switch but I don't believe there is any issue with it and my kitchen under cupboard lights are done this way.
RCD is required, is your ring circuit currently covered? if not the house FCU can be be a RCD type.
The 6mm² SWA seems a bit big for a 13A circuit and his is notifiable work, 2.5mm² is usually good up to around 30m or possibly more so do speak with your electrician to do the cable calculations before starting any work.
Thank you for your advice, and for the praise of my diagram!
The final ring circuit, of which the 13A FCU, starts and ends at a RCD on the consumer unit, which was only fitted about 4 years ago, so this should cover the angles?
The SWA run is about 25 metres.
I used an online calculator on the Doncaster Cables website and that indicated a CSA of 6 sq mm.
If 2.5 sq mm is good for up to 30m then maybe I'm buying myself some wiggle room with 6 sq mm?
Yes I was aware of it being notifiable work.
It has been suggested that I could call in the company that originally fitted my consumer unit and get them to carry out a health check on my electrical circuits etc and slip this new spur in through the backdoor!
My only other concern is the earthing situation.
Does the run need anything extra over and above what is already provided by the house?
There are earthing rods which look a bit OTT, and cable glands with a banjo, but the SWA starts from an IP rated junction box at the house which is IP rated but plastic.
Maybe some better grounding is required at the shed due to its remoteness from the houise?