In brief: my house has an oven circuit with a 6mm cable and a 20 amp MCB. Both the electric hob (6.5 kW) and oven (2.8 kW) are on this circuit. Can I upgrade the MCB to stop it tripping?

Background: We moved in to the house a couple of years ago. The built in oven was slow to heat up so I did a like-for-like replacement, but now the oven circuit trips if the oven is on at the same time as two or three hobs. It turns out it's only got a 20 amp MCB. I now realise it didn't have this problem previously because only one of the three elements of the old oven was working, so it didn't draw much power.

I don't know why the circuit only has a 20 amp MCB. I suspect there used to be a gas hob with an electric oven, and at some stage the hob was replaced with an electric one but the circuit wasn't modified.

I've been told that because there's a 6 mm cable I might be able to replace the MCB to stop it tripping as easily. Is that right, and if so, how high can I safely go? 30 amp? 45 amp etc? I don't know how long the cable is, but I guess not very long as the consumer unit is just outside the kitchen. The oven is 2.8 kW and the hob is 6.5 kW, so a total of 9.3 kW.

Long term we plan to redo the kitchen and sort out the wiring at the same time. I'm looking for a safe, functional, interim measure in the meantime.
 
The standard cooker circuit is 30 or 32A, wired in 6 milli.
9.3kW is 40.43A but diversity is allowed on a cooker circuit, so 32A is fine.

However, what make and model is your board? You may find it difficult to get a matching breaker.
 
Thanks securespark. It's a Wylex consumer unit although I can't see the model. I don't think the same MCB is still available now but Screwfix etc sell Wylex MCBs with the same pins. I trust that's okay?
 