There has been some talk about ovens on a large supply, the standard UK supply to a cooker is 32 amp and there is no problem connecting an oven to a 32 amp supply unless the manufacturer says other wise.
However at what point there is a problem is a subject for debate, clearly with the cable sizes in an oven you would not use a 100 amp supply, but as to a 40, or 45 amp supply I am really not sure, what we want is should a cable work loose and fall off or an element go short circuit it will fail safe.
In real terms it would likely touch some thing earthed and trip the RCD, however we are told we should not rely on the RCD, so personally I would not want to supply an oven with over 32 amp, but can't find any regulations to support that.
But be it a twin cable or single cable if they come from same protective device then make no difference, the only reason for two cables is so an oven over 3 kW can be protected with an overload of a reasonable size, under 3 kW we can use a FCU but over it needs to come from the CU as you can't get an overload device local of a reasonable size. My mother had a second CU in the kitchen so kitchen supply independent to rest of house.
You can get twin cooker connection units so you can power hob and oven from same supply, my stand alone cooker can draw 60 amp however it is on a 32 amp supply as the manufacturer recommends and the MCB (old house) and RCBO (new house) has never tripped, so clearly a 32 amp supply is ample.
The induction hob can deliver more power than a hot plate, but it wastes less power, so in real terms the total use of power drops, as heats the pan not the house, so personally I would supply both from 32 amp supply.
You could daisy chain the cables using a cooker supply unit, clearly wired in parallel but I understand what you mean wired in series.
It does not matter size of isolator as long as larger than size of supply, it is the fuse/MCB/RCBO size that matters. I think no problem in England to do as you say, in Wales the LABC charges would mean not worth while, better to use a scheme member electrician.