I have connected up a new 5 KW instant water heater and have used 4mm cable of about 4 metres long to connect to the modern Wylex consumer unit with 2 RCDs using a 32 amp circuit breaker.
The manual for the water heater suggests that it draws 22 amps or so, but the 32 amp breaker was to hand.
As soon as I switch the water heater on, the RCD trips and cannot be reset unless the heater is switched off.
The wiring is correctly installed.
The resistance of the heater element shows as 12 ohms, so I assumed that was OK.
I then disconnected the live and neutral from the element but the RCD immediately tripped out again when the heater was switched on.
I then tried separately disconnecting the live and then the neutral feed to see what happened.
Disconnecting the live feed made no difference, the RCD tripped, but disconnecting the neutral feed allowed the heater to be switched on without tripping the RCD.
I've past my limit of knowledge here and have no idea how to proceed.
Any help gratefully received.
The manual for the water heater suggests that it draws 22 amps or so, but the 32 amp breaker was to hand.
As soon as I switch the water heater on, the RCD trips and cannot be reset unless the heater is switched off.
The wiring is correctly installed.
The resistance of the heater element shows as 12 ohms, so I assumed that was OK.
I then disconnected the live and neutral from the element but the RCD immediately tripped out again when the heater was switched on.
I then tried separately disconnecting the live and then the neutral feed to see what happened.
Disconnecting the live feed made no difference, the RCD tripped, but disconnecting the neutral feed allowed the heater to be switched on without tripping the RCD.
I've past my limit of knowledge here and have no idea how to proceed.
Any help gratefully received.