Replacing Honeywell ST9100a with Hive

Joined
28 Sep 2021
Messages
2
Reaction score
0
Country
United Kingdom
Hi everyone,

We are just in the process of a kitchen refit and have purchased a hive (single channel).

Having removed the face place for the existing programmer (Honeywell ST9100a) I have noticed more wiring than I had expected, for example multiple cables in Earth, Live and Neutral.

Looking at the wiring diagram I was under the impression that when fitting the hive I would just need to reposition the wiring as the below, however the extra wires has thrown me off a bit.

Earth -> Earth
N -> N
L -> L
1 -> 1
4 -> 3

There is also an existing thermostat which I intend to leave on full for the moment.

Has anyone got any thoughts?

Cheers,
Luke
 

Attachments

  • Capture.JPG
    Capture.JPG
    18.6 KB · Views: 556
  • PXL_20210927_181725364.jpg
    PXL_20210927_181725364.jpg
    281.5 KB · Views: 362
  • Hive.jpg
    Hive.jpg
    29.9 KB · Views: 368
Last edited:
Transfer all wires the same, but slight difference as follows:

L to L
N to N
Earth’s to Earth’s
1 to Common (1)
4 to 3 heating on

That’s it.
 
The wires in 1&4 on the existing now go to 1&3 on the hive, you might find that the L&N as they are doubled , will be difficult to fit in the Hive terminals, , as the hive terminals are very tight, if that is the case use terminal strip , and extend single wires to the L&N, you can put the earths in the terminal strip too if you want as the hive doesnt need an earth
 