Hi guys
A few months ago the boiler stopped working and it turned out to be a blown F1.6A fuse on the PCB. Replaced that and it carried on working fine for a few months.
Last night however again it blew the fuse but now when i replace the fuse everything is ok until i call for hot water or the central heating comes on. Yesterday it would work for a few minutes then the fuse would blow. I have connected the pump on its own with a 3A fuse in the plug and it runs fine.
I have removed the fan which moves fine, doesnt make any noise but when i put it back, the fuse blows instantly after hot water is called.
Could it be the fan? Ive inspected the PCB visually and there is no buildup or anything like that.
Help!