The diagram is wrong.It was right according to the diagram
I have a phase rotation meter, so when sent to fit a three phase socket I tested it to ensure correct rotation, however what I didn't do was check other sockets in the building, they were all wired wrong direction.
And when I careful wired a socket for truck freezers to plug into I found the units were inverter controlled so it did not matter which way around it was wired.
I know at building of Sizewell "B" it was a real problem, as extension leads were plugged into extension leads and if concrete pump went wrong way, it would often be corrected in the wrong lead, so we used a phase rotation meter on every socket and every lead to ensure correct one was changed, but I think that is the only job where I have really used a phase rotation meter.
Was that in the 16th edition which would have been valid at the time? Original 20th century version.Reg 643.9
It shall be verified that the phase sequence is maintained at all relevant points throughout the installation
Reg 643.9
It shall be verified that the phase sequence is maintained at all relevant points throughout the installation
I recall "some years ago" at a previous job, we were having some large (to us) chillers installed. So usual stuff, local sparkies arrange a supply and connect it into the unit, then manufacturer's engineer comes to commission it.Sometimes you wire these things up in the right colour sequence, and the motor goes backwards, so you still might have to swap two phases over, but we all that basic stuff.