I know the limit is one spur from a socket on a ring main. Is this a spur to a double socket? If so, is a spur to two singles back to back in a stud partition ok. I would have thought this would be similar to one double.
is a spur to two singles back to back in a stud partition ok
Actually there is no such regulation. You could run two separate spurs, as long as you fully considered the loading of the ring. However, as above, putting it all on the ring is much better.I know the limit is one spur from a socket on a ring main.
Socket to 'em, EFLI.Two separate spurs to the same position would seem to be rather - what's the word? - pointless?
With all the above provisos -
Two separate spurs to the same position would seem to be rather - what's the word? - pointless?
Use 4mm² cable.
Nothing like proper planning, and having as a pervasive influence the concepts of "just in case...", and "but what if...", is there.The situation is as follows. I have a long partition wall and near to one end there is a socket on each side of the wall, back to back. One of these is on the ring and the other is spurred off with a short length of cable through the wall. I have recently over-clad both sides of the wall with plasterboard which has now been skimmed over. Before I clad one side, I ran a length of 2.5mm to the other end of the wall. The idea was that I wanted a socket at the other end of the wall and would not be using the original spur. Therefore I was going to disconnect the original spur and wire up the new socket as a spur instead. However, I would now like an additional socket on the other side of the wall as well which was why I asked the question. Getting another cable to the far end of the wall would now be very difficult. Both the sockets will be used for table lamps.
Wouldn't an FCU still be needed?If not, get two 5A sockets - and plugs for the lamps.
http://www.screwfix.com/p/round-pin-socket-5a-white/92273
Yes, one would still be a spur from a spur......Wouldn't an FCU still be needed?