So those who have seen my previous post know that I now own a Megger MFT 1730 what has recently been calibrated and that I was also experiencing higher than permitted Zs for my kitchen circuit what is protected by a 32A Type B MCB.
With my MFT1730, this is what I get from the same socket in the kitchen!:
3 Wire No-Trip setting = 1.08Ω
2 Wire No-Trip setting = 0.06Ω
Ze + (R1 + R2) = 0.74Ω (L-E link with R2 Socket Adapter)
Ze is 0.16Ω (Measured at CU using 2-Wire high current setting with main pipe bonding disconnected.)
Socket tested is about 25 Meters in cable length away from CU and is wired in 4.0mm² T&E. (Estimate). 2 and 3 Wire Np-Trip tests were done while the circuit was live.
So now for my questions:
1) Are No-Trip/low current loop readings normally that dramatically different from Ze + (R1 + R2)?
2) Why was the 2 Wire No-Trip reading so stupidly low?
3) Did doing the No-Trip tests on alive loaded circuit affect the readings?
Regards: Elliott
Edit: http://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=51169 & Yes I do have the MK 7860s RCD's.
With my MFT1730, this is what I get from the same socket in the kitchen!:
3 Wire No-Trip setting = 1.08Ω
2 Wire No-Trip setting = 0.06Ω
Ze + (R1 + R2) = 0.74Ω (L-E link with R2 Socket Adapter)
Ze is 0.16Ω (Measured at CU using 2-Wire high current setting with main pipe bonding disconnected.)
Socket tested is about 25 Meters in cable length away from CU and is wired in 4.0mm² T&E. (Estimate). 2 and 3 Wire Np-Trip tests were done while the circuit was live.
So now for my questions:
1) Are No-Trip/low current loop readings normally that dramatically different from Ze + (R1 + R2)?
2) Why was the 2 Wire No-Trip reading so stupidly low?
3) Did doing the No-Trip tests on a
Regards: Elliott
Edit: http://www.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=51169 & Yes I do have the MK 7860s RCD's.