U-value for new external wall on a new small extension

Joined
10 Feb 2022
Messages
23
Reaction score
1
Country
United Kingdom
Hi, I want a small extension to accommodate a 2x1m bathroom (internal area) and a 1.5x1m service area. I'd like an external brickwork, in terms of appearance, to blend with the rest of the house (cavity wall from 1970).

What is the U-value requirement for the new external walls, please?
Am I looking at the right document below (doc L, vol 1: Dwellings, 2021 w/ 2023 amendments)?

On page 35, table 4.2 says the requirement is 0.18 W/(m2·K) U value, which would require 400mm-ish thick walls. Is my understanding correct?
Isn't it too much for an extra bathroom and service area?

It also says:
"If meeting such a standard would reduce the internal floor area of the room bounded by the wall by more than 5%, a lesser provision may be appropriate"

Ok, but what constitutes a lesser provision?
It doesn't point to any explanation. Can I consider as appropriate whatever U-value I want?
Is this what we pay tax for? For them to create difficult, unclear regulations? Gosh!!!

It's a side extension and I want to leave a foot passage to the backyard, therefore I'm trying to make the extension as narrow as it can be.
In the worst-case scenario, I think about accessing it via an external door, despite being an adjoining extension, just to be considered a non-habitable space and lessen the requirements, etc.. but only if necessary and if it makes sense.

I appreciate any help, please.
Thanks.
 
Hi, I want a small extension to accommodate a 2x1m bathroom (internal area) and a 1.5x1m service area. I'd like an external brickwork, in terms of appearance, to blend with the rest of the house (cavity wall from 1970).

What is the U-value requirement for the new external walls, please?
Am I looking at the right document below (doc L, vol 1: Dwellings, 2021 w/ 2023 amendments)?

On page 35, table 4.2 says the requirement is 0.18 W/(m2·K) U value, which would require 400mm-ish thick walls. Is my understanding correct?
Isn't it too much for an extra bathroom and service area?

It also says:
"If meeting such a standard would reduce the internal floor area of the room bounded by the wall by more than 5%, a lesser provision may be appropriate"

Ok, but what constitutes a lesser provision?
It doesn't point to any explanation. Can I consider as appropriate whatever U-value I want?
Is this what we pay tax for? For them to create difficult, unclear regulations? Gosh!!!

It's a side extension and I want to leave a foot passage to the backyard, therefore I'm trying to make the extension as narrow as it can be.
In the worst-case scenario, I think about accessing it via an external door, despite being an adjoining extension, just to be considered a non-habitable space and lessen the requirements, etc.. but only if necessary and if it makes sense.

I appreciate any help, please.
Thanks.
Using a more powerful (and more expensive) insulation, walls can be successfully built using 300mm thick walls, i.e. 105mm - 100mm - 100mm (external brickwork - cavity - internal blockwork).
Full fill Unilin for example.
 