Hi, I am installing a DSC PowerSeries PC1832 panel and having trouble disarming.
With the alarm set, when I enter via a delay zone I am unable to disarm the system with the user code. After the delay the alarm enters the alarm state, at which point I am able to stop the alarm with the user code.
I have recorded a video showing the problem:
1. Arm with code
2. Exit via delay zone
3. System arms
4. Enter via delay zone
5. System starts entry delay
6. Enter user code - Alarm does not disarm
7. Alarm sounds after delay ends
8. Enter user code during alarm
9. System disarms with alarm occurred report
If I enter an incorrect code the screen tells me this.
I have tried setting up a an additional user code, but the same issue occurs whether trying to disarm with the master code or the additional user code.
If I arm the system, I am able to disarm with the code if the delay zone is not tripped:
It's a DSC PC1832
Have tried the entry/exit zone set to type 01 (delay 01) and 34 (final door set)
I'm using DEOL setup.
The door contact sensor has a built in resistor at 4.7k, not the 5.6k as provided by DSC - but it senses open/close fine and tamper is not triggered. No system troubles are showing.
There is only this (1) zone connected to the system for testing, as zone 09 (zone 1 on the first PC5108 card)
All other 32 zones are set to 00 null.
There is one keypad and two PC5108 cards installed.
Thanks for your help, as I am gutted to be stumped this early on in the install and testing!
With the alarm set, when I enter via a delay zone I am unable to disarm the system with the user code. After the delay the alarm enters the alarm state, at which point I am able to stop the alarm with the user code.
I have recorded a video showing the problem:
1. Arm with code
2. Exit via delay zone
3. System arms
4. Enter via delay zone
5. System starts entry delay
6. Enter user code - Alarm does not disarm
7. Alarm sounds after delay ends
8. Enter user code during alarm
9. System disarms with alarm occurred report
If I enter an incorrect code the screen tells me this.
I have tried setting up a an additional user code, but the same issue occurs whether trying to disarm with the master code or the additional user code.
If I arm the system, I am able to disarm with the code if the delay zone is not tripped:
It's a DSC PC1832
Have tried the entry/exit zone set to type 01 (delay 01) and 34 (final door set)
I'm using DEOL setup.
The door contact sensor has a built in resistor at 4.7k, not the 5.6k as provided by DSC - but it senses open/close fine and tamper is not triggered. No system troubles are showing.
There is only this (1) zone connected to the system for testing, as zone 09 (zone 1 on the first PC5108 card)
All other 32 zones are set to 00 null.
There is one keypad and two PC5108 cards installed.
Thanks for your help, as I am gutted to be stumped this early on in the install and testing!