Hi, some years ago I had wet UFH installed in my conservatory. It was just chopped into the existing Y plan wiring and plumbing. The problem being that when UFH demands the CH/HW runs and vice versa. We have put up with it but now as we are spending more time at home it needs fixing.
The best solution would be changing it to an S plan but that would require major plumbing work. The overflow and cold feed are just before the pump in the upstairs airing cupboard and the boiler in the garage. So, as it stands, I can’t put a 2-port valve in line to the HW/CH as it would block the overflow.
The UFH has a 2-port valve on the return and a mixer and pump on the flow controlled by a separate room stat.
Am I right in thinking that the simplest solution would be to attach a relay to both the switched live from the CH/HW to the boiler and the switched live from the otherwise separate UFH stat/2 port valve/pump.
Any comments appreciated. Thanks
The best solution would be changing it to an S plan but that would require major plumbing work. The overflow and cold feed are just before the pump in the upstairs airing cupboard and the boiler in the garage. So, as it stands, I can’t put a 2-port valve in line to the HW/CH as it would block the overflow.