Hi,
My Compact 24 gives hot water for about 2 minutes then cuts out. CH works absolutely fine. Pressure etc all good. Dial turned up full for DHW. Tried reducing the flow into the boiler a couple of turns but no difference.
Measured the resistance across both NTCs giving the following:
DHW - 17k cold, 4.6k after the couple of minutes it runs for
CH - 17k cold, 3.6k after running for 20 minutes
17k is slightly higher than room temperature spec presumably because ambient is colder just now?
http://gasboilerforums.com/thermistoreadingsR-W.html
Any thoughts on whether these readings point to the DHW NTC being at fault? Don't fancy draining the system to replace a part in-spec. Do wonder why the CH NTC isn't going as low as the specified 1.5k though.
Thanks!