Hi all as the title says I have an issue with my boiler taking ages to ignite with either the heating or hot water. I’ve gone through the fault finding on the service manual and want to check with you guys before I spend a bit of money.
At start up the fan runs and the air pressure switche is getting 24Vdc back to the PCB, terminal CN8.4 and CN8.5, so that is ok then according to the manual I should be getting 230Vac at terminals CN6.1 and CN6.2 for the spark electrode. With the sparker connection removed I am only getting 50-60Vac. My guess is I need a new ignition board, would you agree?
Thanks in advance for your help
At start up the fan runs and the air pressure switche is getting 24Vdc back to the PCB, terminal CN8.4 and CN8.5, so that is ok then according to the manual I should be getting 230Vac at terminals CN6.1 and CN6.2 for the spark electrode. With the sparker connection removed I am only getting 50-60Vac. My guess is I need a new ignition board, would you agree?