wago connecters

Joined
18 Feb 2019
Messages
3
Reaction score
0
Country
United Kingdom
hi I need to blank off 2 double sockets in a room that is going to be used as a bathroom. would 24 amp rated wago connecters be suitable to use . thanks stuart
 
Which specific Wago connectors are you referring to?

If the room is to be converted to a bathroom, the sockets and the cabling need to be completely removed, not just 'blanked off'.
 
hi I was referring to the 221 series I was planning on burying them in the wall but is that against the regs
 
They would then likely not be in a "safe Zone" depicted by an accessory ie the socket so not allowed.
 
Those connectors and others like them are only maintenance free when correctly installed into a suitable maintenance free enclosure.
Cables must remain in zones defined by the accessories, so just hiding them in the wall is not permitted.

The cables need to be removed completely.
 
hi flameport / 333 rocky 333 thanks for the advice I will now be removing the sockets / cable from the room. really apricate the sound advice that you have given thanks stuart
 